What size generator should you get?...
|
|
Generators should be installed by qualified electricians. Most generators are rated in watts. The formula for watts is Watts=Volts x Amps. If you you have a 120 watt bulb at 120 volts you would have one amp. If you were to run 25 100 watt bulbs you would need a 2,500 watt generator. Motor circuits such as circulating motors for heat and compressors for refrigerators must be calculated differently. It takes about three times the current to start a motor. Most motors have the amperage rating on the name tag. If the motor has a nameplate rating of 3 amps you might want to add 9 amps on your generator calculations. Also because most generators may run over a period of time you may not want to run at full capacity. About 80% of the wattage rating of your generator would be the way to go. There are a few things to consider when getting a generator. |